RE: Как посмотреть температуру компонентов сервера?


Главная Форумы POWER Systems AIX/Hardware Как посмотреть температуру компонентов сервера? RE: Как посмотреть температуру компонентов сервера?

#1397

andrewk
Участник

выяснил подробности у наших бойцов — у них тоже нет никаких environmental attributes, как оказалось. Они смотрят на Reference Code на HMC. Пока нарылись следующие reference codes:

11007203 — Ambient temperature exceeded limit
The system will shut down in 15 minutes. Follow the instructions for the items listed in the FRU List.

11007201 — Ambient temperature is out of range
Follow the procedure for the items listed in the FRU List.

11007205 — Ambient temperature exceeded limit
The system will shut down in 20 seconds. Follow the instructions for the items listed in the FRU List.

Procedure in FRU list (AMBTEMP):
The system detected a room ambient over-temperature warning or fault.

1. Is the room temperature less than 35 degrees C or 95 degrees F?
* No: Notify the customer. The customer must bring the room temperature within normal range. Continue with the next step.
* Yes: Continue with the next step.
2. Are the system front and rear doors free of obstructions?
* No: Notify the customer. The system must be free of obstructions for proper air flow. Continue with the next step.
* Yes: Continue with the next step.
3. If applicable, do all the positions in the processor subsystem contain processors or fillers?
* Yes: Continue with the next step.
* No: Fill any open positions with processors or fillers. This ends the procedure.
4. Do all the power supply positions contain power supplies or fillers?
* Yes: Continue with the next step.
* No: Fill any open positions with supplies or fan books. This ends the procedure.
5. Are you working with reference code 7201?
* Yes: This indicates that the room temperature is too high. The customer must bring the room temperature to less than 35 degrees C or 95 degrees F. If the room temperature is less than 35 degrees C or 95 degrees F, continue with the next step. This ends the procedure.
* No: Continue with the next step.
6. Perform the following:
* For model 8203-E4A, 9407-M15, 9408-M25, exchange the control panel. Use the following table to determine the part number for the field replaceable unit (FRU). Then continue with the next step.
CCIN or FFC Type and model Part number Description Location code
8203-E4A, 9407-M15, 9408-M25 10N9737 Control (Operator) panel U n-D1
* For model 8204-E8A, 9409-M50, exchange the control panel. Use the following table to determine the part number for the field replaceable unit (FRU). Then continue with the next step.
CCIN or FFC Type and model Part number Description Location code
8204-E8A, 9409-M50 42R5505 Operator panel U n-D1
* For model 9406-MMA or 9117-MMA, exchange processor 1 and processor 2, one at a time, until either the problem is resolved or you have replaced both processors. Then continue with the next step.

For each unit, starting with the primary unit and then the secondary units, use the following table to determine the part number for the field replaceable unit (FRU):
CCIN or FFC Type and model Part number Description Location code
9406-MMA, 9117-MMA 10N9146 3.5 GHz POWER6™ — 2 core processor book U n-P2-C1
9406-MMA, 9117-MMA 10N9144 4.2 GHz POWER6 -2 core processor book U n-P2-C1
9406-MMA, 9117-MMA 10N9139 4.7 GHz POWER6 -2 core processor card U n-P2-C1
7. After each FRU is exchanged, is the error code that sent you to this procedure still reported?
* No: The problem has been corrected. This ends the procedure.
* Yes: Replace the next FRU on the list. If all FRUs on the list have been replaced, call your next level of support. This ends the procedure.

11007211 — Ambient temperature is out of range
Ambient Temperature is above nominal for CPU performance. Follow the instructions for the items listed in the FRU List.

Procedure in FRU list (AMBTMP1):

Ambient air temperature is too high for optimal performance.

Air used for cooling the unit is above the temperature at which the unit is designed to run at maximum performance. The following checks will help determine the problem:

* If the room temperature is above the specified range for the unit reporting this problem, then take steps to lower the room temperature.
* If the air being drawn into the unit is above the specified range, either move the unit to a place where the air is within range, or take steps to reduce the temperature of the air surrounding the unit. This can be accomplished by moving the source of the air that is too warm.
* If the temperature of the air at the unit’s air intake is within the range specified contact your next level of support.

Если найду еще чего-нибудь в доке — напишу