Вот сам в инфоцентре нашёл эти условия:
[code]Attention: In order to use the power on procedure for this model you must check to see if you have one of the following adapters installed in slot P1-C6/C7.

FC 1800 – HSL-2 Ports – 2 Copper
FC 1801 – HSL-2 Ports – 2 Optical
FC 1810 – GX Dual-port 4x HCA

Is one of these adapters present in slot P1-C6/C7?

Yes: Check for a label by the slot that indicates specifically that power supply concurrent maintenance is supported.
If there is no label you must select the power off procedure to prevent system damage or data loss.
If there is a label you can continue with the power on procedure.
No: you can continue with the power on procedure.
[/code]